Recalling parameter sets via RS232/IP ESP+PM

Hi all!

I had a problem with an installation today, with 2 x ESP88 , 1 x PM4250N and two PM8500Ns. 

Recalling a parameter set via RS232 is done correct for the two ESP's (only one is getting the command), but the parts involving the PM amps is not invoked. The parameters change visually correct in CSP designer though...

I did a bit of searching, and found this thread: https://www.bosepro.community/...00n-and-controlspace

Sending the command to all devices(Serial over IP on port 10055) in the parameter set seemed to do the trick.

- This is just not very practical. The correct visual change in CSP designer led me to believe that it worked fine. Wasted quite a long time on-site today trying to figure it out...

Maybe there could be a warning or no visual change for the devices not getting the parameter set change. 

Best regards 

Lars